I should know the answer to this, but since we just got failed by the local inspector, I'll ask for some backup.
He failed us on our transformers which are 480-208Y/120 feeding panelboards. They are in a bar joist ceiling (exposed) and the wire length is probably right at 25'. He cited 240.21(C)(2) and my opinion is we are compliant with 241.21(C)(6). The wire is 500 kcmil copper from our 150 kVA transformer and the primary protection is a 90A C/B. It terminates on a 400 amp C/B in the panelboard, which he also says is a violation (no rounding up in this case ?)
So, I throw this out to the assembled masses and await your opinions.
Thanks
He failed us on our transformers which are 480-208Y/120 feeding panelboards. They are in a bar joist ceiling (exposed) and the wire length is probably right at 25'. He cited 240.21(C)(2) and my opinion is we are compliant with 241.21(C)(6). The wire is 500 kcmil copper from our 150 kVA transformer and the primary protection is a 90A C/B. It terminates on a 400 amp C/B in the panelboard, which he also says is a violation (no rounding up in this case ?)