240.21 Location in Circuit. Overcurrent protection shall
be provided in each ungrounded circuit conductor and shall
be located at the point where the conductors receive their
supply except as specified in 240.21(A) through (H). Conductors
supplied under the provisions of 240.21(A) through (H)
shall not supply another conductor except through an overcurrent
protective device meeting the requirements of 240.4.
You can't use 240.4(B) for transformer secondary conductors, so the author is correct. See 240.21(C)....4/0 75C conductor is only good for 230 amps. Next higher standard overcurrent device would be 250 - this would probably be ok, but would only apply where the primary is allowed to protect the secondary - which is pretty much limited to two wire single phase secondaries or 3 wire delta secondaries, so the 4/0 is considered a tap conductor for all other applications. ...
You can't use 240.4(B) for transformer secondary conductors, so the author is correct. See 240.21(C).
If the transformer in question is a two wire to two wire or a delta/delta then the installation would be code compliant if you increased the 4/0 to 250 kcmil....
I still think I am on track with my thought process though. Lets say the secondary is 250 copper instead of 4/0 and everything else unchanged. Then I believe there would be no violation in that drawing as is. Do you have anything to shoot that down with? ...
If the transformer in question is a two wire to two wire or a delta/delta then the installation would be code compliant if you increased the 4/0 to 250 kcmil.
2 or or 3 wire, I don't see how that changes...
240.21 Location in Circuit. Overcurrent protection shall
be provided in each ungrounded circuit conductor and shall
be located at the point where the conductors receive their
supply except as specified in 240.21(A) through (H). Conductors
supplied under the provisions of 240.21(A) through
(H) shall not supply another conductor except through an
overcurrent protective device meeting the requirements of
240.4.
If the transformer in question is a two wire to two wire or a delta/delta then the installation would be code compliant if you increased the 4/0 to 250 kcmil.
2 or or 3 wire, I don't see how that changes...
240.21 Location in Circuit. Overcurrent protection shall
be provided in each ungrounded circuit conductor and shall
be located at the point where the conductors receive their
supply except as specified in 240.21(A) through (H). Conductors
supplied under the provisions of 240.21(A) through
(H) shall not supply another conductor except through an
overcurrent protective device meeting the requirements of
240.4.
All noteworthy but still not compliant. 240.21(C)(1) says primary protection must be in accordance with 450.3. Table 450.3(B) limits primary only protection of the transformer to 125% of rated current. Drawing shows 90A primary with 125A fuse... that's 139%.Now go farther down in the section you quoted and tell us what you think of what it says in part (C)(1).
All noteworthy but still not compliant. 240.21(C)(1) says primary protection must be in accordance with 450.3. Table 450.3(B) limits primary only protection of the transformer to 125% of rated current. Drawing shows 90A primary with 125A fuse... that's 139%.
Doh!!! I stand corrected (by prompt).Looking at T450.3.B (note 1), what size fuse would you recommend?
ice
Yes, you make a good point. I just see the secondary conductors of a two wire to two wire transformer as protected at their ampacity and not really tap conductors. I know the code does not say that.2 or or 3 wire, I don't see how that changes...
240.21 Location in Circuit. Overcurrent protection shall
be provided in each ungrounded circuit conductor and shall
be located at the point where the conductors receive their
supply except as specified in 240.21(A) through (H). Conductors
supplied under the provisions of 240.21(A) through
(H) shall not supply another conductor except through an
overcurrent protective device meeting the requirements of
240.4.
Single-phase (other than 2-wire) and multiphase (other than delta-delta, 3-wire) transformer secondary conductors are not considered to be protected by the primary overcurrent protective device.
I still say the last sentence of 240.21(C)(1) tells us that a two wire or three wire delta secondary is not a tap conductor.
Four wire (delta-wye) secondaries are not tap conductors either. But it is irrelevant because the code does not say you cannot "tap a tap." It says Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an over current device.
This would include feeder taps, branch circuit taps, busway taps, motor circuit taps, as well as conductors from generator terminals, battery conductors and transformer secondary conductors.
Four wire (delta-wye) secondaries are not tap conductors either. But it is irrelevant because the code does not say you cannot "tap a tap." It says Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an over current device.
This would include feeder taps, branch circuit taps, busway taps, motor circuit taps, as well as conductors from generator terminals, battery conductors and transformer secondary conductors.