Thanks for the replies, but I'm still unclear of the outcome. Is the figure from post #1 an acceptable installation or no?
Not acceptable
The taps are not tapping a tap since transformer secondary conductors are not considered a tap
The taps are tapping "transformer secondary conductors." This is a violation of 240.21.
Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an over current device...
Last edited: