Transformer secondary w/ tap conductors

Status
Not open for further replies.
Thanks for the replies, but I'm still unclear of the outcome. Is the figure from post #1 an acceptable installation or no?

Not acceptable

The taps are not tapping a tap since transformer secondary conductors are not considered a tap

The taps are tapping "transformer secondary conductors." This is a violation of 240.21.

Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an over current device...
 
Last edited: