Re: Transformer Secondary
240.21(C)(2) requires that secondary conductors must land on a device with a rating equal to or less than the conductor ampacity. That is not the case here so this rule does not apply. 240.21(C)(6) requires that the secondary conductors terminate on a single OCPD having a rating equal to or less than the conductor ampacity. Again that is not the case here. I thing that there are 3 code compliant options for this installation:
1) the 600s terminate on a MLO panel with a bus rating of not greater than 420 amps and there are three 225 amp breakers installed to feed the panels,
2) the 600s terminate on a OCPD with a rating of 420 amps or less and then the load side of that breaker is tapped with 3 sets of 4/0 to feed the panels, or
3) one set of 4/0 is run from the transformer to each of the?panels and landed on 225 amp main breakers in the panels.
Don
[ January 08, 2006, 07:44 PM: Message edited by: don_resqcapt19 ]