In general, what size transformer is used for a 3000 amp commercial service. It is 277/480.
Thanks
Just because you have 3000 amps of service conductor/overcurrent protection doesn't mean your actual load ever reaches 3000 amps. Therefore POCO's typically look at the actual demand or at least an estimated demand when installing new. They sometimes even look at peak demand, for how long, and what kind of cooling off period may be normal and take that into consideration, and are willing to push a smaller transformer to certain limits than to use a larger than needed transformer.In general, what size transformer is used for a 3000 amp commercial service. It is 277/480.
Thanks
In general, what size transformer is used for a 3000 amp commercial service. It is 277/480.
Thanks
OP was inquiring about transformer for a service, which generally means POCO's transformer.My clients are industrial. Most own their own transformers. The philosophy generally is:If we can line the system up to where we can pull 3000A, that is what we want.
No we don't want to burn one up every now and then. Down time is way too costly.
Keep the Vd down to where the HIDs don't shut off when large motors start.
We want to run flat out 24/7
We will pay some extra to get the MTBF up
Given these constraints, for a 480V, 3000A secondary main, I would expect the transformer to be 2MVA. FLA ~ 2400A. 2400A X 1.25 = 3000A
Which didn't answer your question, you asked about "commercial". And I don't know.
That's true.OP was inquiring about transformer for a service, which generally means POCO's transformer. ....