If you have a 225 kVA transformer, maximum output on the secondary is 625 amps @ 208/120V.
How would you size the secondary OCPD? 650 amp fuses or 800A fuses if you wanted to assume a continuous load at 125% (781 amps).
The part that I'm questioning / confused about is, if someone down the road sees an 800 amp fused disconnect - is it not wrong for them to assume they can load that up to 800 amps of non continuous load ? But they'll only get 625 amps max out of it.