The load analysis for a church building is 1200A 120/208V 3⌀ , what would be the appropriate transformer size (kVA) should this service require on the power pole.
Note- The energy company installed 3 transformers on the power pole each of them of 75kVA with a total of 225kVA.
In my opinion it should be 3 transformers of 150kVA, due to the formula for a 3⌀ transformer being ((Volts X Amps X 1.732)/1000)=kVA.
Am i correct on the size of the 3 transformers needing to be 75kVA each, or am I wrong bc we transformer kVA shall be calculated based on the actual running load and not on connected load or rated load?