Transformer sizing 3phase 120/208wye - 480 delta
Fordean
New Jersey
Electrical Contractor
I have a project. The new power washer is 60 HP @ 480 Volts @ 48 Amps 3phase
I have to use a stock type transformer. For the one which I spec'd is 14 week out to 10 weeks
I would like to try a 45kva I used a 50 in spec. Only 2 in stock are the 45 KVA and a 75 KVA
I planned on 150 amp tapped from 400 amp main. (1/0 thhn thinking ALum maybe that would be 2/0)
Can someone check my calc.
I calculated the Incoming
208volt 3 phase to 39.9 KW.
480volt 48a 3phase 19 kw
Calculations appear to be way off. 19kw @ 480v3 phase is 22 amps. 48amp would be 40kw,
The 45kva would possibly be "light" for a motor load.
I would suggest sizing transformer at a minimum of 125% of FLC out of NEC.
I don’t know much about sizing trannys for motor loads but I know during the locked rotor current of the start up of the motor if not sized large enough you could have extreme voltage drop resulting in a motor not starting.
I'd recommend double checking the motor data. A 60 hp, 460 V 3-phase motor has an NEC FLA (430.250) of 77 A. 1 kVA per hp is generally a good rough approximation. So 60 hp would be about 60 kVA. This is 72 A at 480 V.
Something seems off on the motor data.
You were right. Its not 60 its 48.8 HP. Got confused with other job. Picture is below.
side note: I looked at the operating instructions and spec sheet and, it may be generic, but the install instructions call for GFCI protection.
Something to think about
KVA should be same both sides of the transformer. Rated amps is what will change. A 45KVA unit should be rated 125 amps on low volts side and 54 on the high volts side. That should be too small for a 60 HP motor, but I see we concluded this is only a 48 HP motor - getting close but possibly still a little undersized.
Same ideas here. I size transformers 140% of the expected load +, + any other future loads!