Fordean
- New Jersey
- Electrical Contractor
I have a project. The new power washer is 60 HP @ 480 Volts @ 48 Amps 3phase
I have to use a stock type transformer. For the one which I spec'd is 14 week out to 10 weeks
I would like to try a 45kva I used a 50 in spec. Only 2 in stock are the 45 KVA and a 75 KVA
I planned on 150 amp tapped from 400 amp main. (1/0 thhn thinking ALum maybe that would be 2/0)
Can someone check my calc.
I calculated the Incoming
208volt 3 phase to 39.9 KW.
480volt 48a 3phase 19 kw