That makes more sense....... explains why such a large transformer.....
Is this transformer a Power Company transformer or customer owned ?
 

Prototype1

Member
Location
Kansas City
Occupation
Noob EE
Pickleball court – Total Watts – 3,584 (8 lights) - 448 watts each light
Tennis – Total Watts – 2,406 (6 lights) - 401 watts each light
Trail Lights – Total Watts = 1170 Watts (26 Poles lights) - 45 watts each light
Bollards – Total Watts = 760 Watts (20 Bollards lights) - 38 watts each light
Disk Lights – Total Watts = 480 Watts (8 lights) - 60 watts each light


3 circuits from the panel board. 1 going to the pickleball court and plaza lights. 1 going to the tennis court. 1 for the trail lights and bollards.

1st circuit:
Total wattage for the 1st circuit:
3584 watts + 480 watts = 4064 Watts

Apply the 80% continuous load factor.
4064 watts * 0.8 = 3251.2 watts

# of lights: 3251.2 watts / (448 watts/light + 60 watts/light) ~ 6.57 lights
Rounded down: Approximately 6 Pickleball lights and 6 plaza lights.



2nd circuit:
Total wattage for the 2nd circuit:
2406 watts

Apply the 80% continuous load factor.
2406 watts * 0.8 = 1924.8 watts

# of lights:1924.8 watts / (401 watts/light) ~ 4.80 lights
Rounded down: Approximately 4 tennis lights.

3rd circuit:
Total wattage for the 3rd circuit:
1170 watts + 760 watts = 1930 Watts

Apply the 80% continuous load factor.
1930 watts * 0.8 = 1544 watts

# of lights: 1544 watts / (45 watts/light + 38 watts/light) ~ 20.96 lights
Rounded down: Approximately 20 lights (combining Trail lights and Bollard lights). We have total 46 lights trail + bollard lights.

P = I*E
1st circuit: 3521.2 W / 120 V = 29.34 A
2nd circuit: 1924.8 W / 120 V = 16.04 A
3rd circuit: 1544 W / 120 V = 12.87 A
29.34+16.04+12.87 = 58.25 A, and I can use 60 A panel.
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Correct me if I am wrong:
You are adding a relative small load (8.4kw) to an existing 150kva customer owned transformer.
All the wiring is outside.

If that's the case, 240.21(C)(4) applies and you can add a M/B panel adequate for the load. A 60 panel would be more than adequate
(You can, of course, go larger if you want to allow for future loads)
 

Prototype1

Member
Location
Kansas City
Occupation
Noob EE
Yes, to my knowledge the transformer is only feeding the building. In the example drawing I attached. They adding a new conduit, conductors going to the new panel ( after I size it) and from the panel, the conduit/conductors go to the lights and etc. In the future, they will be adding more things on that panel, like 5hp motors, more lights, and etc.
 

Prototype1

Member
Location
Kansas City
Occupation
Noob EE
Till now, I understand that 60 Amp panel is good.
1st circuit: 3521.2 W / 120 V = 29.34 A
2nd circuit: 1924.8 W / 120 V = 16.04 A
3rd circuit: 1544 W / 120 V = 12.87 A

Because my lighting is continuous load,
should I do 29.34 * 1.25 = 36.675 A
16.04 * 1.25 = 20.05 A
12.87 * 1.25 = 16.0875 A

and go to Table 310.16, to size the conductors?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Unless you are already locked in on 120v fixtures I would suggest 208v fixtures. Reduces your current and helps on voltage drop.
 

Prototype1

Member
Location
Kansas City
Occupation
Noob EE
Here is the example drawing. The transformer is existing there and the panels, lights and conduit/conductors are still need to be size.
 

Attachments

  • info lights.JPG
    info lights.JPG
    24.3 KB · Views: 3

Prototype1

Member
Location
Kansas City
Occupation
Noob EE
Unless you are already locked in on 120v fixtures I would suggest 208v fixtures. Reduces your current and helps on voltage drop.
Okay.
1st circuit: 3521.2 W / 208 V = 16.93 A
2nd circuit: 1924.8 W / 208 V = 9.25 A
3rd circuit: 1544 W / 208 V = 7.42 A

Because my lighting is continuous load,
should I do 16.93 * 1.25 = 21.1625 A
9.25 * 1.25 = 11.5625 A
7.42 * 1.25 = 9.27 A

There are very low amps. Table 310.16 does not show wire size for this low. Which other table?
and go to Table 310.16, to size the conductors?
 