Re point #6:
The lower the rating of the transformer, the higher the voltage drop (voltage rise) across the transformer. And the harder it is to properly detect the low impedance of the grid for anti-islanding purposes.
This is intriguing, pardon what may be clueless questions and/or layman's terms...
(point #6 might have something to do with that link I posted in point #1 re:islanding then? Hmm.)
Example equipment is:
1. 3x 24.1kW (29A) inverters, 480Y/277V output, so the 3 inverters = 87A / 72.3kVA.
2. 75kVA xfmr = 480Y/277V to MV (or 208V)
3. (Side note: That'd be a 200A 208Y120V or 100A 480Y/277V "POCO service", but you'd be outputting 87A through a 90.2A/75kVA xfmr, sounds kinda-a-bit-too-close for me. (And 72.3KVA = 200.9A or 200.6A when converted to 208Y/120V...)
With the 72.3kVA/87A of PV the xfmr is running at 96.4% of its 75kVA/100% rating.
So when you said "lower the rating" you meant the 100% xfmr as compared to the PV output?
This lower rating could be said as "higher the (PV:xfmr rating) ratio", or that 96.4% (ratio is 0.964:1).
The xfrmr runs less efficiently at 125% (1.25:1) than it does at 80% (0.8:1), and less efficiently at 96.4% than at 90% or 80% or 65%.
This is because of higher
voltage drop (voltage rise).
The inverter(s) have to detect the
low impedance of the grid.
This low impedance is actually "approaching infinite" on grid side.
When you are going ---> inverter 480Y277V - connected to LV side / air gap/ then grid side /MV side of POCO's xfmr, the impedance of POCO xfmr is a factor.
(Side note: Now, if there is a step-down from inverter-to 208Y/120V xfmr, then another step-up-to-POCO MV xfmr involved, the impedance is MUCH different than straight 480-MV?)
But what I want to know is-
With this voltage drop/rise "across" the xfmr...which is caused by the xfmr being closer to its 100% rating and less efficient/running hotter...
do the inverters "have to"...or...do they "end up"...
decreasing their voltage?
The inverters could have more DC power than they can handle and therefore be clipping, ok.
When so, they still want to put their max (72.3kVA for instance) output into a grid with as little impedance as possible, at as close to 480Y/277V as possible.
When say a 75kVA step-down xfmr is "holding them back" so to speak, it is because...
the xfmr is putting out <208V, and therefore "asking for" <480V from the inverters?
Could one say the 208V impedance is "clogging up" the xfmr on the inverters' side?
Are amps lost to heat because of lower voltage?
-or-
Do I have it backwards and the inverters "have to" or "end up" INCREASING their AC voltage to compensate for lower 208V voltage?
Or!
Does the xfmr just heat up due to physics because 72.3KVA of PV is 96.4% of its 100%, and the windings are more efficient at 90%, and voltage drops on both sides?
Thanks again, if this makes sense...