jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
but what would be happening with H2 from the 480V side and X2 on the 120/240V side?
Don't yell at me!
But I can sort of see how, if current has to go from X2 to X1 and X3, (if that's physically possible) it would cause some serious issues.
Nothing would be happening at X2 because there's nothing at the service to hook it up to. Or rather, anything happening at X2 is just flowing through the transformer coils between X1 and X3 as if there's no terminal at X2.
Ergo on the 480V side there will not be a proper voltage reference, and the inverter will not turn on. And thus nothing would be happening on either side, as far as current flow is concerned. Golddigger or someone else will have to confirm for you what the voltage measurements would be from H2 to other terminals. I could take a guess but I may get it wrong. (Hey, that's something you should try PVfarmer, i.e. keeping your mouth shut when you're not sure of a statement.
Now supposing a 480V 3-phase generator that is not an interactive inverter was hooked up to the 480 side, and somehow properly synced to the grid, then I gather that any loads hooked to the 240/120 phase will draw current. But that's where the 5% problem with the transformer would come in. Again, an engineer could explain why that problem comes up. In any case, iit would be illegal without a transfer switch, and we're just trying to understand theory here because actually doing it would be stupid.