I have calculated 4 offices and 3 apartments to come up to 596.7 amperes 120/208 3 phase. A 225 KVA transformer will give 624 full load amps at 208. The next size up that I know of is a 300 KVA which will give 832 amps full load. Am I pushing it too close to allow the 225KVA? :smile:
I'm going to require the 300 KVA, but could I permit the 225 and be within code?
I'm going to require the 300 KVA, but could I permit the 225 and be within code?