I have a 480 delta to 240v delta transformer with a lighting tap.
Can I run 3 phase and 1 phase breakers in the same loadcenter (subpanel)
I would bring in the x4 lighting tap to an isolated neutral bar, that would be bonded to the ground bar.
obviously I would have to look out for the high leg for my 120 volt taps
thanks
Mike
Also I'm under 10' from transformer to panel, so I the primary OCPD would be all I need ? Or do I need a main breaker in the subpanel ?