If I understand...
If I understand...
You are just asking is strut is ok. I ASSUME that the transformer is to be installed in a fire resistant room transformer room (450.21(B), size over 112.5 kva), and the MFR states it is ok to mount to a wall. ( Note: Not trying to be a stick in the mud, but most of the large transformers I've installed have a MFR's info which states install must be X given distance from a wall to allow for cooling. (450.9) )