I have two sets of secondary conductors from 75kva three phase 480v to 208/120v feeding two panels. Each panel main circuit breaker is 225A. So 225x2 = 450a which is 216% of transformer secondary full load amps.
The primary breaker is sized within 125% of full load amps.
Customer says transformer is protected by primary breaker. No need for secondary breakers at all in terms of transformer protection. The secondary breakers provided for secondary conductor and in accordance with tap rules. The secondary two sets feeding panels demand load is less than 75kva rating now.
The demand load of both panels is less than transformer 75kva rating at present but can exceed if in future they add load to panels to exceed that of the 75kva transformer since btoh panels have room and can add in future.
Is the above allowed in code?
The primary breaker is sized within 125% of full load amps.
Customer says transformer is protected by primary breaker. No need for secondary breakers at all in terms of transformer protection. The secondary breakers provided for secondary conductor and in accordance with tap rules. The secondary two sets feeding panels demand load is less than 75kva rating now.