What is the purpose of primary breaker? In theory would not the primary breaker if sized 125% protect the transformer from overloads?
Yes, that would be the case.
But remember if a transformer was intended to be overloaded, the primary side breaker would be sized based on the larger primary current.
According to Hammond Power Solutions, https://www.hammondpowersolutions.com/faq/can-i-increase-the-kva-rating-of-an-existing-transformer/
"[FONT="]The most common way to increase the available kVA rating of an existing transformer is to add additional fan cooling."[/FONT]