kingpb
Senior Member
- Location
- SE USA as far as you can go
- Occupation
- Engineer, Registered
That is incorrect.winnie said:Meaning that you should get the full KVA of the transformer if you connect 504V to the 504V tap, 480V to the 480V tap, or 456V to the 456V tap. But that doesn't tell us what happens if 480V is supplied to the 456V tap.
-Jon
Assuming taps are on the HV side, and they are the standard 2 x +2.5% and 2 x -2.5% and nominal voltage is 480V, 3ph - applying 480V to the -5% tap (456V) and no-load on the LV side of the transformer will raise the voltage by 5%. So, assuming 208V on LV side, the actual measured voltage would be approx. 219V. Of course ignoring transformer and cable losses. The fact that you change taps does not diminish the rating e.g. it's still a 30KVA transformer.
What will change on the nameplate is that the rated current will inversely go up or down by the same percent as the voltage change.