ok...i asked using the incorrect terms, i apologize...
250.30(A)(7) is what covers it...it's actually the grounding conductor size that i need...
but that is sized according to 250.66
in this installation, we have 2 transformers, one feeds a 150A panel with a set of 1/0...which I can use a #6 from the transformer to the steel...correct?
the 2nd feeds a 200A panel with a set of 3/0...which would require a #4 from the transformer to the steel...correct?
am i reading this correctly?