rh2
Member
- Location
- Dallas, Texas
- Occupation
- Electrical Engineer
We have a new requirement to add a liquid pump (120V, 0.5HP, 8A, M code ~5.7x LRA) to an equipment skid. The skid has a weatherproof controls enclosure that is already used to house a VFD for another process, a PLC, some relays, terminal blocks, and branch circuit protection for various instrumentation. The majority of the power in this enclosure is of course consumed by the VFD (modulation of the 480V mains) and we will have enough mains power from our generator to accomodate the new pump. Inside the enclosure there exists a single phase, type T 0.5kVA instrumentation transformer (Pri=480, Sec=120) that is used to power the smaller things like the PLC and instrumentation. It would be very convenient for us to use the existing footprint that this transformer occupies (about 6"x6") and put, in its place, what I believe should be a 2kVA unit to power everything along with the pump.
My question is simply regarding the type of transformer this is (T) and then any implications within NEC of using a type T for what is now powering a characteristically different load (motor start).
1.) Is this considered "illegal" or an improper type of transformer to employ for this use case? Should I be looking at other types? If a traditional isolation transformer is still OK, should I avoid certain types? (T vs. TF vs. ??)
2.) My understanding is that the 115C rise rating of the currently installed transformer should require me to find the 2kVA transformer in a similar 115C rise rating so as to not introduce a change in the heat dissipation profile of the inside of the enclosure. Should I be wiser in my assumptions?
Thank you
My question is simply regarding the type of transformer this is (T) and then any implications within NEC of using a type T for what is now powering a characteristically different load (motor start).
1.) Is this considered "illegal" or an improper type of transformer to employ for this use case? Should I be looking at other types? If a traditional isolation transformer is still OK, should I avoid certain types? (T vs. TF vs. ??)
2.) My understanding is that the 115C rise rating of the currently installed transformer should require me to find the 2kVA transformer in a similar 115C rise rating so as to not introduce a change in the heat dissipation profile of the inside of the enclosure. Should I be wiser in my assumptions?
Thank you