Transformer voltage drop

Status
Not open for further replies.

saravanan

Member
We have a transformer of 2500KVA and max current is around 3330A. When i start a compressor of capacity 200KW(with soft starter control) with nominal current 320A, compressor takes 1950Amps and voltage coming down to 340V. My source capacity is 8MW. Cable size for the motor is 2 runs of 3 X 300sq mm UG cable. What could be the reason for this voltage drop
 
What sort of 'soft start' control is being used?

How long are the feeders to the compressor?

What sort of motor is used in the compressor?

What is the impedance rating of the transformer?

What is the KVA rating of the source?

What surrounds the motor feeders (steel conduit, soil, open air, etc.)?

Where are you measuring the voltage?

How are you measuring current?

What is the duration of the voltage sag?

Do you have any voltage measurements from the primary side of the transformer?

The number of unknowns in your question greatly exceeds the information provided.

-Jon
 
Is the transformer taps adjusted or are they on he nominal position?

What is the nominal system voltage on the HV and LV side of the transformer?

What is the rated voltage of the compressor?
 
What sort of 'soft start' control is being used? Votage control method

How long are the feeders to the compressor? 75mtrs distance

What sort of motor is used in the compressor? squirrel gage induction motor

What is the impedance rating of the transformer? Impedence voltage 6%

What is the KVA rating of the source? 2500KVA transformer

What surrounds the motor feeders (steel conduit, soil, open air, etc.)? Closed panel

Where are you measuring the voltage? at the compressor end

How are you measuring current? by RMS meter to measure peak current

What is the duration of the voltage sag? about 30 sec

Do you have any voltage measurements from the primary side of the transformer? Yes, from a feeder management relay

The number of unknowns in your question greatly exceeds the information provided.

-Jon[/QUOTE]
 
Is the transformer taps adjusted or are they on he nominal position? it is in normal tap

What is the nominal system voltage on the HV and LV side of the transformer?11KV/415Volts

What is the rated voltage of the compressor? 415V plus or minus 10%
 