A long time ago, I posted about testing a 480 to 120v step down control transformer for ratio as a nuclear plant test technician. We had many that failed because we applied 120 to the secondary and measured for 480 on the primary. We got MANY wrong ratios. Someone here explained why. Reverse it to apply 480 and measure for 120 and they were correct. You might search for the thread. Just because they're rated for step-down, does not mean they'll work as step up and vice versa. Eye opener for me.
they are 25kva, I will run an EGC - I don't see a need for a neutral conductor?
Big mistake. I'm finding that copious amounts of bacon keep my mind sharp (and my body round.)
Do you need a disconnect for the first transformer's conductors near the first transformer and a primary disconnect for the second transformer?