What kind transformer would I need to supply a DC motor controller with 330-360 ( max 400 volt) volt single phase from 240 supply?
I'd probably go for 240V/480V but check what maximum voltage the controller can take. Is the controller regenerative four quad SCR? You might wany more margin if it is.What kind transformer would I need to supply a DC motor controller with 330-360 ( max 400 volt) volt single phase from 240 supply?
It is a 4 quad controller Eurotherm 514c-32 Has max voltage of 415 and 32 amps. I think I want to be around 330-360 voltI'd probably go for 240V/480V but check what maximum voltage the controller can take. Is the controller regenerative four quad SCR? You might wany more margin if it is.
It is a 4 quad controller Eurotherm 514c-32 Has max voltage of 415 and 32 amps. I think I want to be around 330-360 volt