scott501st
- Wisconsin
I'm working on a circuit design problem and need to power a 50hp, 480vac motor from a 208/120 panel. I'm thinking that I could backfeed a transformer but am unsure what i would need to do from that point
New poster - long time engineer, but I still need regular doses of enlightment.---. You will also not want to connect the 120 volt neutral to the XO terminal, you do need to connect the equipment grounding conductor from the 120/208 supply to the transformer case.
What happens if you connect the transformer 208Y primary neutral (Xo) to the system 208V neutral?
I've back fed a few Delta/Wye transformers, feeding the wye side for the primary. And as you said, I've never connected the primary wye point.
The utilities regularly use wye primary transformers connected to an MGN and they seem okay with it.
So, while I agree I wouldn't connect the wye point to the 208V neutral, I don't know why it would cause a problem, or what problems it would cause.
I don't have experience with what happens myself, but if you search this site there have been a few threads more recently addressing this, many of them have had overheating problems with the transformer if they had the 208 volt neutral connected to XO terminal.