Transformer

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Ok a generator is feeding a 45kvs transfomer ehich feeds an ATS which feeds a panel. I was wondering if there is a code as to where they transformer has to be such as close/in sight of the generator or more than likely in the room with the ATS & panels becuase they don't show the location of the transformer.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
The secondary conductors of the transformer must comply with one of the rules in 240.21(C) which will limit the length of the secondary conductors.

Chris
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
The secondary conductors of the transformer must comply with one of the rules in 240.21(C) which will limit the length of the secondary conductors.

Chris

I'm there and looking, thanks. THe code is always worded so comlplicated. I see transfromer secondary conductor but they have for not over 10' and not over 25'
 