Panel LP! is serving a remote transformer. Does the transformer need a primary disconnect adjacent to it?
450.14 Disconnecting Means. Transformers, other than
Class 2 or Class 3 transformers, shall have a disconnecting
means located either in sight of the transformer or in
a remote location. Where located in a remote location,
the disconnecting means shall be lockable, and the location
shall be field marked on the transformer.
2011 NEC.
Panel and transformer are in the same building but different floors.