crossman said:The drawing brings up a question from me. At the panel where the GEC raceway attaches to the panel, say the raceway is EMT with a connector to the panel. Do we actually need a bonding bushing and bonding jumper at the connector, or can we rely on the fitting/panel enclosure/main bonding jumper to serve as the connection to the GEC which is terminated at the neutral bar?
I think we can.
crossman said:...Do we actually need a bonding bushing and bonding jumper at the connector,...?
tryinghard said:Yes I think so, to help example this as well see "Physical protection" .100(A)(6) or Articles 800, 820, & 830, these are installed for the same purpose.
The best installation probably does include an open conductor but I think it would need a plastic bushing at the entrance to any ferrous metallic enclosure. We certainly don't want to eliminate the GEC's purpose and if installed wrong ?An inductive choke can reduce the current flow by 97 percent.?
nakulak said:that graphic doesn't meet the OP, unless I am mistaken. With the flex, you will need a bonding wire and bonding bushings, no ? 348.60 (2005)
tryinghard said:True except it is ensuring the correct sized effective path rather than just mechanical connections. Wouldn't this be the same as a feeder that has EGC with a bond bushing?