Presently working on a 150KW Grid Tied Solar System in Los Angeles - We are using a 150KVA transformer to step up the utility voltage from 208Y to 480Y for the SMA 24 TL Inverters. The transformer is installed outdoors with a 200A Fused AC Disconnect within 10Ft of it, protecting the secondary conductors and a 600A/208V/3P Fused AC Disconnect in the electrical room, approximately 30ft, out of sight of the transformer, protecting the primary conductors. My inspector is requiring me to add a second AC Disconnect, close to the transformer, to protect the 208V Conductors [viewed interchangeably as primary or secondary conductors according to him per 690.9(B)]. I believe the installation satisfies the requirements of 450.3 for transformers, and 240.21 for the protection of primary and secondary conductors. The transformer is installed outdoors so the length of primary or secondary conductors shouldn't matter (at least in my opinion).
The crux of the matter seems to be the intent of 690.9(B). In a PV Application, which is primary and secondary of the transformer? Is PV powered produced (480 side) the primary or is it the utility 208 side? Are the primary and secondary interchangeable depending on how it is viewed? Is the additional AC Disconnect Required or not?
The crux of the matter seems to be the intent of 690.9(B). In a PV Application, which is primary and secondary of the transformer? Is PV powered produced (480 side) the primary or is it the utility 208 side? Are the primary and secondary interchangeable depending on how it is viewed? Is the additional AC Disconnect Required or not?