transformer primary protection
transformer primary protection
Im sory for making you confuse...and the term that i'd use.
Ourpower utility (driven by steam) delivers 4160v for every MCC that we have...now from MCC has its own transformer to step down to 460v (DELTA)...
Now im confused for the contractors protection to transformer down to loads. The transformer that id said is a DELTA-DELTA connection. From MCC to loads 460/230v. now on their design primary CB is 150A which is 125% of the x'former rated primary current...and 400A CB for secondary (computed from loads)
wire size is 1-50sq mm and 95sq mm on primary and secondary 1-180sq mm...assuming primary cables are correct, is this two cables used are complying 145sq mm cable requirement