gar
- Ann Arbor, Michigan
- EE
090311-1623 EST
The question of using a step down transformer in the reverse direction seems to pop up fairly often. Today I ran a quick check on one transformer. This is a Sq-D SKC B-4 0.5 KVA.
The primary can be wired 480 or 240. I wired it 240.
The secondary can be wired 240 or 120. I wired 240.
Thus a nominal 1 to 1 transformer. I ran this at 120 V instead of 240 because that was easy. Also ran the transformer unloaded.
The resistance of the normal primary = 2.7 ohms.
The resistance of the normal secondary = 3.3 ohms.
Obviously the design of the primary is to reduce power dissipation in the primary from the magnetizing current.
Used in the normal direction
120 V input
125 V output
Apparent turns ratio 125/120 = 1.042
Used in the reverse direction
120 V input
114.8 V output
Apparent turns ratio 120/114.8 = 1.045
This is a good correlation.
Used in the reverse direction I believe the KVA and KW capability will be slightly reduced because the power dissipation will be greater in the 3.3 ohms than in the 2.7 ohms.
Clearly the transformer is wound to provide slightly higher open circuit voltage on the secondary than one would select just on the basis of desired output voltage.
120 V input
125 V output
120 V input
114.8 V output