I've been wiring for a while now and have had this question in the back of my mind. Wiring a 3phase transformer from an existing panel say 480 volts to 208/120, is considered a Separately Derived System.
In Ca. I install a ground rod and run a ground wire to the water line where it enters the building and usually bond the neutral in the trans.
OK, here's the question. If I install a transformer that's dedicated to one machine only, say 208 3 phase to 480 3phase.
Transformer may not be installed by the machine. Is it still considered a Separately Derived System and needing a water line ground and ground rod
or just a ground wire run in conduit with phase conductors as water line grounds run across buildings can get expensive.
Some machines from other countries have transformers as part of the machine .
We just run power to the safety switch like 3 phase with ground and were done
My names Carl
Just found this site on the web and I think it's very cool.
I've been wiring for a while now and have had this question in the back of my mind. Wiring a 3phase transformer from an existing panel say 480 volts to 208/120, is considered a Separately Derived System.
In Ca. I install a ground rod and run a ground wire to the water line where it enters the building and usually bond the neutral in the trans.
OK, here's the question. If I install a transformer that's dedicated to one machine only, say 208 3 phase to 480 3phase.
Transformer may not be installed by the machine. Is it still considered a Separately Derived System and needing a water line ground and ground rod
or just a ground wire run in conduit with phase conductors as water line grounds run across buildings can get expensive.
Some machines from other countries have transformers as part of the machine .
We just run power to the safety switch like 3 phase with ground and were done