Transformers
HDHeritage
New member
Calif.
Hi,
My names Carl
Just found this site on the web and I think it's very cool.
I've been wiring for a while now and have had this question in the back of my mind. Wiring a 3phase transformer from an existing panel say 480 volts to 208/120, is considered a Separately Derived System.
In Ca. I install a ground rod and run a ground wire to the water line where it enters the building and usually bond the neutral in the trans.
OK, here's the question. If I install a transformer that's dedicated to one machine only, say 208 3 phase to 480 3phase.
Transformer may not be installed by the machine. Is it still considered a Separately Derived System and needing a water line ground and ground rod
or just a ground wire run in conduit with phase conductors as water line grounds run across buildings can get expensive.
Some machines from other countries have transformers as part of the machine .
We just run power to the safety switch like 3 phase with ground and were done
Hi Carl, welcome to the Forum.
Does it fit this defination?
Separately Derived System. A premises wiring system whose power is derived from a source of electric energy or equipment other than a service. Such systems have no direct electrical connection, including a solidly connected grounded circuit conductor, to supply conductors originating in another system.
And many that are still built in this country have transformers intergral also. You are not installing these transformers.
I still wonder about this all the time. It seems like no one can give me a straight answer. Just today we had a contractor come and install a 480/120-240 Single Phase Dry XFMR. They only ran 2 ungrounded + 1 grounding wire from our 480 V MDP. They were supplying a 120/240 100 Amp CH Lighting Panel.They ran the grounding wires to a lug tapped to the XFMR case. They didn't bond in either the dry xfmr, nor the 100 Amp panel. From what I have learned/been taught, is that you bond either/or, but not both. Any clarification?
Not to mention....We have fully capable military electricians, yet we had to pay a contractor to put this in? I was angered, especially when I have been twiddling thumbs lately!
Oh yeah....also....I would say where I work is an industrial environment....everything is either 277/480 volt, or stepped down to 120/208....yet my upper management decided for this upgrade....to install 120/240 single phase. I was pretty mad when I heard this...because most likely in 6 months, they will find something to buy, and the only available power now is 120/240 Single phase. IMO, nothing like shooting ourselves in the foot!