Jubert Lowe
Member
I am installing temporary power on a site I have a 277/480v 3-phase step down transformer that I would like to use, the problem that I am having is I have 480v single phase from the utility company, so when I hook up to H-1 & H-2 from the utility company and my secondary X-1 & X-2 between X-1 and X-0 it read 120v but between X-2 and X-0 it read 78v between both it reads 198v, what could I do to get 120v on each I don't want to purchase a single phase transformer.
Thanks
Jubert
Thanks
Jubert