You either need to corner ground your HV delta, or provide ground fault alarming.is their a grounding issue, I see no reason either ia is actually putting out 441 volts on the high tap and it is a multitap transformer
I see no reason to call it illegal without additional information. Of course, you do realize you will only have 416V on the output unless the transformer has taps that provide a 208:480 ratio.
I'm not discussing the code issues, just a physics question (and a transformer design question):
240 is right at 20% above the design input. Wouldn't this tend to drive the core into saturation? I don't know what size this transformer is, but aren't most small "comodity" transformers (say below 100kva) built as light on iron and copper (or aluminum) as the mfg can do? This is my reasoning why the increased voltage would tend to drive the core into saturation.
cf
Steve66 is correct, they are feeding a 240V coil with only 80% of voltage. This will impact the loading capacity of the transformer. Because a transformer is basically a motor that does not turn, voltage variances will be similar to a voltage starved motor.I'm not discussing the code issues, just a physics question (and a transformer design question):
240 is right at 20% above the design input. Wouldn't this tend to drive the core into saturation? I don't know what size this transformer is, but aren't most small "comodity" transformers (say below 100kva) built as light on iron and copper (or aluminum) as the mfg can do? This is my reasoning why the increased voltage would tend to drive the core into saturation.
cf
No, just a problem with my dyslexic reading.cf, from a physics standpoint, do you see a problem connecting a 240 volt transformer to a 208 system ?
If I were guessing - I'd guess he is using the one he has....I'm wondering why you would want to do this? Are you trying to drive 480V loads? Why not get a transfromer with the right voltage ratings??