My question is if you have a 480 volt step down xformer to 208 can you wire it back words by feeding the secondary at 208 and get 480 out , .
if so do you need the netural on the 208 side.
When using a standard step-down transformer in reverse.
You most likely will wnd up corner grounding the output. But you must ensure that all connected devices on the high voltage side have a straight 480 vac rating and not a 480/277v rating. There will be two phases that are each 480 volts to ground, and one phase that is now a grounded conductor.
Does this mean tying one of the H# lugs to the case and ground?
Yes, but not only. It should be wired like any grounded conductor, white or gray insulation/marking, not fused unless OCP opens all conductors, etc.Does this mean tying one of the H# lugs to the case and ground?