transfrmer grounding

Status
Not open for further replies.

MBLES

Senior Member
i need to install a 50kva transformer on seventh floor parking garage. i dont have any building steel available. the transformer is feed from first
floor. could i run GEC in same conduit as feeder to ground rod on first floor? any ideas welcome.
 
i need to install a 50kva transformer on seventh floor parking garage. i dont have any building steel available. the transformer is feed from first
floor. could i run GEC in same conduit as feeder to ground rod on first floor? any ideas welcome.

I think you would have to bond it to the conduit at both ends if it is ferrous, but I don't recall any requirement that precludes putting a GEC in a conduit with other conductors.

Incidentally, the code requirement is not to bond it to building steel but to the closest available grounding electrode.
 
Is the transformer fed from the service equipment?