We use TVSS (MOV) in our VFD cabinets; we have been connecting it to the line side of main breaker feeding the cabinet. I see 2 problems with this: (1)-there will be potentially energized cables in cabinet even if breaker is open and (2)-MOV may get damaged before a breaker upstream to VFD main breaker (which has higher trip rating) trips. There is nothing of our concern upstream to VFD main breaker that we'd want to protect against transient voltage. So I am thinking of moving the MOV to the load side of main breaker. Anyone sees anything wrong with this?
Your opinion is appreciated.