According to 515-2 a Class I location shall not extend beyond a floor wall or roof. (Bulk Storage Plants)
I am installing small scale processing equipment where ethanol will be prevalent and the area will be Class I Div I. I am planning on having most of the electrical support equipment (Vac pumps, oil recirc etc.) in an adjacent equipment shed which is basically what the NEC suggests in 500-3 -a -FPN "Through the exercise of ingenuity in the layout of electrical installations for haz locations, it is frequently possible to locate much of the equipment in less haz or nonhaz locations...."
Is the 515-2 standard applicable. Does the equipment in this adjacent building have to meet any special classification. Electrical will be passing through two metal walls and entering into the classified processing area.
There will be no "communicating openings" between the processing building and he equipment shed.
Does my equipment shed need to be any minimum distance from the processing area? Can the shed be considered unclassified?
I am installing small scale processing equipment where ethanol will be prevalent and the area will be Class I Div I. I am planning on having most of the electrical support equipment (Vac pumps, oil recirc etc.) in an adjacent equipment shed which is basically what the NEC suggests in 500-3 -a -FPN "Through the exercise of ingenuity in the layout of electrical installations for haz locations, it is frequently possible to locate much of the equipment in less haz or nonhaz locations...."
Is the 515-2 standard applicable. Does the equipment in this adjacent building have to meet any special classification. Electrical will be passing through two metal walls and entering into the classified processing area.
There will be no "communicating openings" between the processing building and he equipment shed.
Does my equipment shed need to be any minimum distance from the processing area? Can the shed be considered unclassified?