.....We have rule and measures for reasons like you can't parallel any conductor smaller than a 4/0......
My Bad, I knew that didn't sound right and didn't look it up.
Thanks![]()
Uh-oh, sounds like the onset of CRS.No, it was a senior moment.
I couldn't remember.
.....Larry crs does mean control system right?![]()
Take a look at 300.3(B).
Chris
I can read that as saying that "if I am not using the grounded conductor, then I need not install it in the conduit."(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4).
Hello Gus and Don
....Tom no it doesn't have a thing to do with magnetic fields, what ever give you that idea?
Ronald![]()
I can read that as saying that "if I am not using the grounded conductor, then I need not install it in the conduit."
... - I'm looking at what appears to be a hole in the language.