I sthere any code requirement for travelers in 3 ways having the neutral run with them? or is it just a design consideration? Looking for specifics or your opinions. Thanks
Stew,stew said:I sthere any code requirement for travelers in 3 ways having the neutral run with them? or is it just a design consideration?
Metallic; it matters.stew said:how about when using mc cable?
LarryFine said:Metallic; it matters.
Read 300.3(B)(3) last sentence (from the NEC, not my link above).LarryFine said:Metallic; it matters.
infinity said:On a dead end 3-way it would not matter even with MC cable. The neutral is not required.
infinity said:On a dead end 3-way it would not matter even with MC cable. The neutral is not required.
You guys misunderstood my answer. I wasn't saying that a neutral is required to be run to a switch; I was saying that, in my example of a switch loop, the return leg (and not a neutral) should be run in the same cable, that MC is a metallic method, and therefore these rules apply.al hildenbrand said:Read 300.3(B)(3) last sentence (from the NEC, not my link above).
The fine print note under 300.20(B) is particularly interesting.2005 NEC
300.3(B)(3) Conductors of single-conductor Type MC cable with a nonmagnetic sheath shall comply with the provisions of 330.31, 330.116, and 300.20(B).
Keep in mind that if the travellers are run between switches "nonferrously" and unaccompanied by other conductor(s) of the circuit, the hot and switch leg must also be run "nonferrously" where they are unaccompanied. Note that "other conductor(s) of the circuit" as mentioned here must be of a conducting portion of the local circuit. Also note that in using the nonferrous method, the individual conductors should not run parallel and adjacent to any ferrous materials, such as a steel stud.stew said:yes that was the way they were goig to do it. 3 phase 120/208 and the neutral was going to be the one common to the 3 circuits a,b and c.I ran a 12/3 mc however because it just didnt seem right to me but I again dont really know that it matters except for the metallic wirng method taht has been pointed out.
What is the NEC reference?Smart $ said:Also note that in using the nonferrous method, the individual conductors should not run parallel and adjacent to any ferrous materials, such as a steel stud.
If the MC cable is aluminum, there is no "sufficient" induced current in the aluminum to cause heating, even when the circuit inside the aluminum sheath is only a single conductor (worst case).stew said:but I again don't really know that it matters except for the metallic wiring method that has been pointed out.
From KO to KO, so the result is effectively a single hole that all of the conductors pass through.al hildenbrand said:The NEC doesn't tell us how long the notch is to be.