Well, this was a new one on me....
Got a service call that a GFCI kept popping. Went on site and replaced the GFCI outlet. Lady started up her Peloton and 5 seconds later it popped again. I scratched my head and stuck in another just in case and that popped.
Well I'll be...Googled it up, and sure enough, about 20-30 hits for these darn things, including their own website!
Peloton states that they drain the static electricity from their belt out the grounding conductor so it will pop GFCI protected circuits! So they recommended using their products only on dedicated non-GFCI protected circuits!
https://support.onepeloton.com/hc/e...92-Peloton-Tread-and-Tread-Usage-Requirements
Seeing as these things are generally installed in basements, which are required to have GFCI protected circuits, how are they proposing you get around the NEC?
I had to leave her without a solution as I couldn't remove the GFCI and violate the NEC.
Thoughts?
Got a service call that a GFCI kept popping. Went on site and replaced the GFCI outlet. Lady started up her Peloton and 5 seconds later it popped again. I scratched my head and stuck in another just in case and that popped.
Well I'll be...Googled it up, and sure enough, about 20-30 hits for these darn things, including their own website!
Peloton states that they drain the static electricity from their belt out the grounding conductor so it will pop GFCI protected circuits! So they recommended using their products only on dedicated non-GFCI protected circuits!
https://support.onepeloton.com/hc/e...92-Peloton-Tread-and-Tread-Usage-Requirements
Seeing as these things are generally installed in basements, which are required to have GFCI protected circuits, how are they proposing you get around the NEC?
I had to leave her without a solution as I couldn't remove the GFCI and violate the NEC.
Thoughts?