Re: trick question!
I have to add the there is one breaker that's really not a tandem breaker but they serve the same purpose. The slim line GE mini breaker, I stopped using these several years ago as the 20 amp one seem prone to failure at the contact point on the buss. The one good thing is these panels also have the stabs for full size breakers which is what I used with the last ones we had in stock. Just can't put as many in it.
The other thing is the original question was
This come from article 100 for branch circuit-Multiwire:

I have to add the there is one breaker that's really not a tandem breaker but they serve the same purpose. The slim line GE mini breaker, I stopped using these several years ago as the 20 amp one seem prone to failure at the contact point on the buss. The one good thing is these panels also have the stabs for full size breakers which is what I used with the last ones we had in stock. Just can't put as many in it.
The other thing is the original question was
This would only be called a multiwire circuit if there is a voltage between both ungrounded conductors, and a voltage between each ungrounded conductor and the grounded conductor. Most tandems would not support this today.Can you feed multiwire circuits from a "Tandem" 20-20 circuit breaker?
This come from article 100 for branch circuit-Multiwire:
So if it is not a multiwire circuit then 210.4 or 240.20(B)(1) would not apply You would think that 300.13(B) should apply but if you cant call it a multiwire circuit as per article 100 then it would be one of those tuff callsBranch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them , and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.