So 1amp is 540ft round trip? So ~270ft of ckt.All about conduit fill for upsizing the wire for VD. Total circuit length is 540 ft total from source to load and back. That adds up depending on if, for example, I use #8's or #10's.
I am still however confused as to what you are doing. Replacing the old with new for bigger pipe? All new to the side of what's there? How much of 270ft is buried?
Bury sched 40, make the risers sched 80. Not clear to me how many feet you have to go from above grade to some connection point, but just figure from the turn up in the trench to above ground end point use sched 80. Done.
At retail sched 80 is about 1.8x that of sched 40 in 2", and about 1.6x for 1/2".