Digitrp RMS 510 Trip Unit
Digitrp RMS 510 Trip Unit
Yesterday when replacing some bulbs on the switchgear that indicate if breaker is open or closed i notice the digatrip had a flashing red lite on the ground fault indicator and though the breaker should have tripped open . I have seen a flag on a trip unit before which showed a fault and the breaker never opened because of poor maintenance and this seems to be the same situation.
Does anyone have an idea if this breaker should have opened on the indicating ground fault light ?
Several years ago I was called out on a similar situation. Below is an excerpt from the field service report. Although the trip unit tested ok on the self-test, we concluded that it was a nuisance indication and ended up replacing the trip unit.
1. ApparatusIdentification 2. Time In/Type of Service 3. Scope of Work to be performed 4. As Found Conditions 5. Work Done and Status of Job 6. Results & Recommendations
1. HSP, I.E.M. 4000A, 480/277V, 3-Phase, 4-Wire, S.O. 046186-001, Main Breaker ?Commercial Breaker #2?, Cutler-Hammer, SPB-100 Insulated Case Circuit Breaker, Cat# SPBR340R, 4000A Frame, with Digitrip 510 Trip Unit Cat# S56LSIG(D), 4000A Plug, Cat# RP6S40A400, In = 4000A.
2. Six years/ charge customer.
3. Investigate the Ground Fault Trip Light indication on the ?Commercial Breaker #2? Main Breaker.
4. BACKGROUND:
Customer reported that during a walk thru on the previous day he noticed the Ground Fault Trip LED indication on the ?Commercial Breaker #2? Main Breaker.
There was no recollection that the breaker had tripped.
5. WORK DONE:
? The Main Breaker was inspected and the Ground Fault Trip LED was found lit with the breaker closed.
? The customer was asked if there were any 277V lighting circuits fed from this breaker and if there was any recent work done on these circuits. He indicated that there was work done on the lighting but was not sure if it was fed by this breaker.
JOB STATUS:
The Ground Fault Trip LED will be reset after a time can be scheduled to properly test the Main Breaker trip unit to determine its integrity.
6. CONCLUSIONS and RECOMMENDATIONS:
? The Main Breaker trip unit has the following trip functions:
1. Long Time Delay
2. Short Time Delay
3. Instantaneous
4. Ground Fault
In the event that the breaker trips on a fault, one of the above LEDs lights to indicate the type of fault that caused the trip. In this case the Ground Fault LED lit but the breaker did not trip. This is an indication that the trip unit may be defective. Another possibility is that the trip unit sensed a ground
fault on the system but did not trip the breaker. A third possibility is that the LED indication is a result of the last self test performed over a year ago and was never reset. In any case, SFE recommends the following:
1. Order a new trip unit.
2. Schedule a time whereby the load fed from this breaker can be transferred to the generator and perform a self test on the trip unit. Based on the results of the test it could be determined if the trip unit needs to be replaced.