Hello All,
Question about effects of 3rd and other triplen harmonics. I have a situation where large SCR based drives are running motors. The existing system had them operational with the previous generator. The generator was replaced in kind (as in KVA) and even with a larger starting KVA capacity. A PMG type exciting system is used on the new generator. Now when the generator tries to run the SCR drives and run the motors it begins surging and then the control system stops (probably due to sensing the surges and dips in the power system). A drive isolation transformer was placed in line on the output of the generator to see if it helps the situation. It in fact did allow the generator to operate without incident.
Detail on the ATS: The ATS is an overlapping neutral type.
My questions is the following. Typically SCR based drive systems produce large 5th and 11th harmonics rather than 3rd and triplen harmonics. To my understanding delta wye transformers (what the drive isolation transformer is) do a good job at trapping the 3rd and triplen harmonics. That being said, my question is if the major source of harmonic distortion is from 5th and 11th harmonics which are negative sequence harmonics, then why when the transformer is connected and filters the triplen harmonics does the installation work? Could it be that the little bit of triplen harmonics found were putting the generator over the edge?
Furthermore, is there any possibility that the generator is not wired correctly, i.e. not having its neutral conductor bonded to ground since it is a separately derived system due to the overlapping neutral ATS? If that is the case could it be that by installing the transformer they are actually providing the neutral connection to ground and this is what is actually eliminating the harmonic destructive results? Could the installation possibly work if it is found out that the neutral on the generator is not grounded since it is mis wired and simply a neutral to ground electrode connection is made?
The reason why I am concerned about the neutral is because I know that the zero sequence triplen harmonics live in the neutral. And due to the complication with the overlapping neutral conductor and possibility for mis-wiring, I hope that not having the neutral connected to ground is somehow exacerbating the situation.