Hello is triplex the same as USE wire? Recently someone told me that 4/0 triplex is good for 240a. But i am unsure what temperature column to use to size it.
I am trying to see what amperage 4/0 triplex is good for on a 2-family overhead service thanksIf this is an NEC application, you can only use the ampacities found in the NEC.
Overhead ...small detail.I am trying to see what amperage 4/0 triplex is good for on a 2-family overhead service thanks
What is the calculated load?I am trying to see what amperage 4/0 triplex is good for on a 2-family overhead service thanks
So regardless of what 4/0 triplex is rated for its still only rated for 180a at 75°c correct?For NEC application, can't you use table 310.20 for the ampacity of triplex in free air (this is a table for ampacity on a messenger wire, up to 3 current carrying conductors). The ampacity of a conductor depends on many things. The primary one being its insulation temperature rating. But even if it is rated for 90C or 150C or 250C, are your terminations rated for that? And voltage drop will quickly get you too if there is any length to this run.
The ampacity of 4/0 aluminum @ 75C is 224A in table 310.20, 280A in table 310.17, and 180A in table 310.16
I don't think that there is any triplex that has an insulation type found in Table 310.4 (310.104 in older codes).Depends. We don’t know if the product you are using has insulation listed in the NEC.
Is there a situation when using 4/0 triplex in pvc for the vertical portion leading to a weatherhead for a 200a service that the 4/0 wire would be rated for more than 180a?Depends. We don’t know if the product you are using has insulation listed in the NEC.
Is there a situation when using 4/0 triplex in pvc for the vertical portion leading to a weatherhead for a 200a service that the 4/0 wire would be rated for more than 180a?
Seemingly adds more complications. Aerial installations often get by with triplex such as "Portunu" as shown in your Post #8 even though it is not a NEC recognized conductor. The wiring in a vertical riser to your weatherhead on the otherhand is almost always required to be a NEC Art 310.104 recognized conductor. 4/0 XHHW or THWN-2 AL would be rated at 180 amps (75°C) and is often used on 200 amp servicesIs there a situation when using 4/0 triplex in pvc for the vertical portion leading to a weatherhead for a 200a service that the 4/0 wire would be rated for more than 180a?
So does using any "triplex" wire of any sort vs say XHHW in the vertical riser to the weatherhead have any advantage?Seemingly adds more complications. Aerial installations often get by with triplex such as "Portunu" as shown in your Post #8 even though it is not a NEC recognized conductor. The wiring in a vertical riser to your weatherhead on the otherhand is almost always required to be a NEC Art 310.104 recognized conductor. 4/0 XHHW or THWN-2 AL would be rated at 180 amps (75°C) and is often used on 200 amp services