Different reasons I have found for nuisance tripping AFI breakers........
1) Ground to N connection
2) Misties in muti-gang switch boxes with more than 1 neutral source wir in them.
3) Rare but.....bad AFI breaker
4) Nail or screw in wire
5) Wrong neutral terminated on breaker in panel.
6) Loose neutral connection in panel(screw completeley backed off)
and, my # 1 favorite of all times....Customer was using her chrome bath bar fixture as a necklace tree. Gold chain was thrown over two lampholders, was contacting neutral screwshell of 1 lamp and chrome grounded chrome fixture shroud on the other lamp. I will admit it took me a little while to find this one.
Also, when troubleshooting, rather than start at the end of the circuit and work your way back to the homerun, start in the middle of the circuit (if you know how the circuit is routed). That way, you will be 1/2 done checking device connections after your 1st one. Good luck.