Yes, you ABSOLUTELY need to coordinate the trip settings. In fact trip settings and values of all protective devices in your system must all be coordinated. Sounds as though you need to have someone come in and do a coordination study.
FXD6 breakers are a 250A frame, so it’s entirely possible that the mag trip units in those two breakers are different. That would mean that the trip settings mean different things.
FXD6 breakers are a 250A frame, so it’s entirely possible that the mag trip units in those two breakers are different. That would mean that the trip settings mean different things.