jason sleeth
Member
- Location
- Illinois
I was wondering when you derate for number of conductors and ambient temperature you have a double derate. You have to derate the wires ampacity for the number of wires then take that derated number and derate it for the ambient temperature. I am being told that if the load is continous you have to derate from your double derated number. I disagree. The way that I understand the code is that you have to take your double derate. You also have to calculate the available ampacity of the conductors if the load is continuos. (@ 80%). Then you compare the two numbers and have to use the more stringent of the two. You do not triple derate your wires. I was wondering what others think on this topic?