winnie
Senior Member
- Location
- Springfield, MA, USA
- Occupation
- Electric motor research
Here is an old Eaton article on slash rated breakers:
How do you sell a product very few people want? Make it illegal not to use it.Yes but it's being enforced.
I need to know the why.
Put in a 3p breaker or step up to a 277/480v breaker where a 2p breaker is needed just to satisfy a voltage rating that seems to already cover the voltage? Seriously?
There's got to be a better reason.
JAP>
How do you sell a product very few people want? Make it illegal not to use it.
It has to do with the breakrrs internal ability to safely clear a fault.
A fault on a 120V to ground circuit can be cleared fairly easily so the breakers can be made cheaply
As the voltage nears 240V to ground the internal arcing paths need to be changed resulting in a more expensive internal construction.
Same here our POCO no longer has it availableFortunately in my area 240v Delta High leg services are quickly becoming a thing of the past.
I never was a big fan of em anyway.
JAP>
Back to the OP, what kind and brand of panel is it? If it is a bolt-on style panel board then yes you can use a 277/480 breaker, for example with Siemans it would be a BQD. If it's a stab on, I'm pretty sure everyone makes a straight rated breaker. For Siemens it has an R suffix, i.e. Q230R (I recently priced them they are about a hundred bucks). For SQ D it's an H suffix, i.e. QO230H. Not sure what the part number is off hand for Joseph Eaton. All three poles are straight rated so you can also use a three-pole. (Some of this has already been mentioned, just summarizing).I am trying to find a 240v breaker vs 120/240 breaker for buddy of mine. This is because they are replacing a breaker for a water heater and one of the phases is the high leg delta. I suppose worse case scenerio they can go with a 277/480 rated 2 pole breaker if it can fit the panel board, am I correct on this? there is no code violation on using this correct?
QO - H series is a 240 volt rated breaker. To get a 277/480 rated breaker in Square D current offerings you need to go to the NF series breakers, they will not fit in a QO series panel, so to use one you will be installing a NF panelboard, can't just bolt it on to panelboard with QO bolt on bus types.Back to the OP, what kind and brand of panel is it? If it is a bolt-on style panel board then yes you can use a 277/480 breaker, for example with Siemans it would be a BQD. If it's a stab on, I'm pretty sure everyone makes a straight rated breaker. For Siemens it has an R suffix, i.e. Q230R (I recently priced them they are about a hundred bucks). For SQ D it's an H suffix, i.e. QO230H. Not sure what the part number is off hand for Joseph Eaton. All three poles are straight rated so you can also use a three-pole. (Some of this has already been mentioned, just summarizing).
And it likely cost same or more than the three pole anyway.Don’t know of any that will install in a 240 volt panel. Like MTW posted, use a three pole if you have the room.
That seems like a dumb design. With Siemens, the 240V bolt ons (B230) are physically the same as the 480 bolt ons (BQD230, of course there are other 480 ones, the BQD's are just the basic standard ones). In fact I have ordered 120/208 panelboards and had it come with a mix of B and BQD breakers.QO - H series is a 240 volt rated breaker. To get a 277/480 rated breaker in Square D current offerings you need to go to the NF series breakers, they will not fit in a QO series panel, so to use one you will be installing a NF panelboard, can't just bolt it on to panelboard with QO bolt on bus types.
That would allow the 240 volt breaker to bolt into the 480 volt panel. And you know that there likely is some installed that way somewhere.That seems like a dumb design. With Siemens, the 240V bolt ons (B230) are physically the same as the 480 bolt ons (BQD230, of course there are other 480 ones, the BQD's are just the basic standard ones). In fact I have ordered 120/208 panelboards and had it come with a mix of B and BQD breakers.
I hate it when that happens.. . . someone may probe me wrong . . .
That would allow the 240 volt breaker to bolt into the 480 volt panel. And you know that there likely is some installed that way
I guess but who cares, someone could put in the correct voltage breaker but a much larger amperage than the conductors. Or one with an under rated AIC. How far do we go to try to brother-in-law proof something? I like the Siemens design because it results in more interchangeable parts. Also it is often prudent to use a 480 breaker on a 208 system where you need a high AIC (a BQD has an AIC of 65k @240v). And of course there is this exact case we are talking about of a Delta system with 208 to ground. But anyway, thanks for the correction I just assumed everybody's 480 breakers were the same as their 240 bolt-ons. Anyone know offhand if this is true for Eaton and GE? I think it's a TEY for a typical GE 480 breaker, will that fit in their 240 volt bolt-on panel boards?That would allow the 240 volt breaker to bolt into the 480 volt panel. And you know that there likely is some installed that way somewhere.
They don't make 240 volt fuses that fit in a 600 volt fuse holder. (Edit: someone may probe me wrong, and I do know of some miniature fuses that will interchange here)
Square D's exception to this is the I-Line series panels and breakers. But your typical DIY or jack of all trades maintenance man isn't messing with those as often as the other series panels either.
Aliens...I hate it when that happens.
And really, what's the stop someone from using a 240 volt panel board on a 480 system? Never underestimate the brother-in-law. I saw that once, guy was putting a square d load center on a 480 systemI have seen that at a few plants I have worked at, panels full of 240V breakers on a 480V system. Some sparky trying to make a few extra $, and putting personal at risk for the savings.
I looked at one job, brand new store (takeover existing building) someone put in an entire 208 volt switchgear on 480 volts! Gear had to be less than 10 years old. How they got it past inspections and energized I don’t know, unless the inspector didn’t know it was going to be 480. Had to give a quote on ripping it out and replacing.And really, what's the stop someone from using a 240 volt panel board on a 480 system? Never underestimate the brother-in-law. I saw that once, guy was putting a square d load center on a 480 system